Welcome to Westonci.ca, where curiosity meets expertise. Ask any question and receive fast, accurate answers from our knowledgeable community. Our platform provides a seamless experience for finding reliable answers from a knowledgeable network of professionals. Join our platform to connect with experts ready to provide precise answers to your questions in different areas.
Sagot :
Answer:
hello your question has a missing information
The other is Δ-connected with an impedance of (60 - j45) ohm per phase.
answer : A) 5A ∠0° ,
p( real power ) = 1800 and Q ( reactive power ) = 0 VAR
B) 193.64 v
C) current at load 1 = 2.236 A , current at load 2 = 4.472 A
D) Load 1 : 450 watts(real power ) , 600 VAR ( reactive power )
Load 2 : 1200 watts ( real power ), -900 VAR ( reactive power )
Explanation:
First convert the Δ-connection to Y- connection attached below is the conversion and pre-solution
A) determine the current, real power and reactive power delivered by the sending-end source
current power delivered (Is) = 5A ∠0°
complex power delivered ( s ) = 3vs Is
= 3 * 120∠0° * 5∠0° = 1800 + j0 ---- ( 1 )
also s = p + jQ ------ ( 2 )
comparing equation 1 and 2
p( real power ) = 1800 and Q ( reactive power ) = 0 VAR
B) determine Line-to-line voltage at the load
Vload = √3 * 111.8
= 193.64 v
c) Determine current per phase in each load
[tex]I_{l1} = Vl1 / Zl1[/tex]
= [tex]\frac{111.8<-10.3}{50<53.13}[/tex] = 2.236∠ 63.43° A hence current at load 1 = 2.236 A
[tex]I_{l2} = V_{l2}/Z_{l2}[/tex]
= [tex]\frac{111.8<-10.3}{25<-36.87}[/tex] = 4.472 ∠ 26.57° A hence current at load 2 = 4.472 A
D) Determine the Total three-phase real and reactive powers absorbed by each load
For load 1
3-phase real power = [tex]3I_{l1} ^{2} R_{l1}[/tex] = 3 * 2.236^2 * 30 = 450 watts
3-phase reactive power = [tex]3I_{l1} ^{2} X_{l1}[/tex] = 3 * 2.236^2 * 40 = 600 VAR
for load 2
3-phase real power = [tex]3I_{l1} ^{2} R_{l2}[/tex] = 1200 watts
3-phase reactive power = [tex]3I_{l1} ^{2} X_{l2}[/tex] = -900 VAR

The sum of load powers and line losses, 1800 W+ j0 VAR and The line voltage magnitude at the load terminal is 193.64 V.
(a) The impedance per phase of the equivalent Y,
[tex]\bar{Z}_{2}=\frac{60-j 45}{3}=(20-j 15) \Omega[/tex]
The phase voltage,
[tex]\bold { V_{1}=\frac{120 \sqrt{3}}{\sqrt{3}}=120 VV }[/tex]
Total impedance from the input terminals,
[tex]\bold {\begin{aligned}&\bar{Z}=2+j 4+\frac{(30+j 40)(20-j 15)}{(30+j 40)+(20-j 15)}=2+j 4+22-j 4=24 \Omega \\&\bar{I}=\frac{\bar{V}_{1}}{\bar{Z}}=\frac{120 \angle 0^{\circ}}{24}=5 \angle 0^{\circ} A\end{aligned} }[/tex]
The three-phase complex power supplied [tex]\bold {=\bar{S}=3 \bar{V}_{1} \bar{I}^{*}=1800 W}[/tex]
P =1800 W and Q = 0 VAR delivered by the sending-end source.
(b) Phase voltage at load terminals will be,
[tex]\bold {\begin{aligned}\bar{V}_{2} &=120 \angle 0^{\circ}-(2+j 4)\left(5 \angle 0^{\circ}\right) \\&=110-j 20=111.8 \angle-10.3^{\circ} V\end{aligned} }[/tex]
The line voltage magnitude at the load terminal,
[tex]\bold{\left(V_{ LOAD }\right)_{L-L}=\sqrt{3} 111.8=193.64 V(V }[/tex]
(c) The current per phase in the Y-connected load,
[tex]\bold {\begin{aligned}&\bar{I}_{1}=\frac{\bar{V}_{2}}{\bar{Z}_{1}}=1-j 2=2.236 \angle-63.4^{\circ} A \\&\bar{I}_{2}=\frac{\bar{V}_{2}}{\bar{Z}_{2}}=4+j 2=4.472 \angle 26.56^{\circ} A\end{aligned} }[/tex]
The phase current magnitude,
[tex]\bold {\left(I_{p h}\right)_{\Delta}=\frac{I_{2}}{\sqrt{3}}=\frac{4.472}{\sqrt{3}}=2.582 }[/tex]
(d) The three-phase complex power absorbed by each load,
[tex]\bold {\begin{aligned}&\bar{S}_{1}=3 \bar{V}_{2} \bar{I}_{1}^{*}=430 W +j 600 VAR \\&\bar{S}_{2}=3 \bar{V}_{2} \bar{I}_{2}^{*}=1200 W -j 900 VAR\end{aligned}}[/tex]
The three-phase complex power absorbed by the line is
[tex]\bold{\bar{S}_{L}=3\left(R_{L}+j X_{L}\right) I^{2}=3(2+j 4)(5)^{2}=150 W +j 300 VAR }[/tex]
Since, the sum of load powers and line losses,
[tex]\bold {\begin{aligned}\bar{S}_{1}+\bar{S}_{2}+\bar{S}_{L} &=(450+j 600)+(1200-j 900)+(150+j 300) \\&=1800 W +j 0 VAR\end{aligned} }[/tex]
To know more about voltage,
https://brainly.com/question/2364325
We hope our answers were helpful. Return anytime for more information and answers to any other questions you may have. Thanks for stopping by. We strive to provide the best answers for all your questions. See you again soon. Thank you for using Westonci.ca. Come back for more in-depth answers to all your queries.