Discover the answers to your questions at Westonci.ca, where experts share their knowledge and insights with you. Explore comprehensive solutions to your questions from knowledgeable professionals across various fields on our platform. Join our platform to connect with experts ready to provide precise answers to your questions in different areas.

A heat pump is used to heat a building. The external temperature is lower than the internal temperature. The pump's coefficient of performance is 3.70, and the heat pump delivers 7.27 MJ as heat to the building each hour. If the heat pump is a Carnot engine working in reverse, at what rate must work be done to run it

Sagot :

Answer:

Heat pump needs 1.965 megajoules each hour to run.

Explanation:

The Coefficient of Performance ([tex]COP[/tex]), no unit, of a Carnot's heat pump is:

[tex]COP = \frac{Q_{H}}{W}[/tex] (1)

Where:

[tex]Q_{H}[/tex] - Heat received by the building, measured in megajoules.

[tex]W[/tex] - Work needed to run the heat pump, measured in megajoules.

If heat pump is a Carnot engine working in reverse, then the amount of work needed to run the heat pump is the least possible work. If we know that [tex]Q_{H} = 7.27\,MJ[/tex] and [tex]COP = 3.70[/tex], then the amount needed by the heat pump each hour is:

[tex]W = \frac{Q_{H}}{COP}[/tex]

[tex]W = \frac{7.27\,MJ}{3.70}[/tex]

[tex]W = 1.965\,MJ[/tex]

Heat pump needs 1.965 megajoules each hour to run.

Your visit means a lot to us. Don't hesitate to return for more reliable answers to any questions you may have. We appreciate your time. Please come back anytime for the latest information and answers to your questions. Keep exploring Westonci.ca for more insightful answers to your questions. We're here to help.