Westonci.ca is the premier destination for reliable answers to your questions, brought to you by a community of experts. Explore thousands of questions and answers from a knowledgeable community of experts ready to help you find solutions. Discover in-depth answers to your questions from a wide network of professionals on our user-friendly Q&A platform.

A three-phase transformer connection has a delta-connected secondary, and one of the transformers has been center-tapped to form a neutral conductor. The phase-to-neutral value of the center-tapped secondary winding is 120V. If the high leg is connected to a single-phase load, how much voltage will be applied to that load

Sagot :

Answer:

207.84 V will be applied to that load.

Explanation:

Given that;

The phase-to-neutral value of the center-tapped secondary winding is 120V

the high leg is connected to a single-phase load

voltage that will be applied to that load = ?

Now, the the high leg voltage will be 1.732 times the single phase center tapped voltage .

so

Load Voltage = 1.732 × 120V

Load Voltage = 207.84 V

Therefore, 207.84 V will be applied to that load.