Welcome to Westonci.ca, the place where your questions find answers from a community of knowledgeable experts. Discover in-depth solutions to your questions from a wide range of experts on our user-friendly Q&A platform. Connect with a community of professionals ready to help you find accurate solutions to your questions quickly and efficiently.

A single-phase 60-Hz overhead power line is symmetrically supported on a horizontal cross arm. Spacing between the centers of the conductors acing between the centers of the conductors (say, a and b) is 2.5 m. A telephone line is also symmetrically supported on a horizontal cross arm 1.8 m directly below the power line. Spacing between the centers of these conductors (say, c and d) is 1.0 m.

4 x 10^7 ln âDad. Dln/Dnk. Dtet

where, for example, Dud denotes the distance in meters between conductors a and.

a. Hence, compute the mutual inductance per kilometer between the power line and the telephone line.
b. Find the GO-Hz voltage per kilometer induced in the telephone line when the power line carries 150 A.

Sagot :

Complete question is;

A single-phase 60-Hz overhead power line is symmetrically supported on a horizontal cross arm. Spacing between the centers of the conductors acing between the centers of the conductors (say, a and b) is 2.5 m. A telephone line is also symmetrically supported on a horizontal cross arm 1.8 m directly below the power line. Spacing between the centers of these conductors (say, c and d) is 1.0 m.

The mutual inductance per unit length between circuit a-b and circuit c-d is given as 4 x 10^(-7) ln √((D_ad × D_bc)/(D_ac × D_bd)) H/m

where, for example, D_ad denotes the distance in meters between conductors a and d.

a. Hence, compute the mutual inductance per kilometer between the power line and the telephone line.

b. Find the 60-Hz voltage per kilometer induced in the telephone line when the power line carries 150 A

Answer:

A) M = 1.01 × 10^(-4) H/km

B) v_cd = 5.712 V/km

Explanation:

A) From the distances given in the question, we can deduce that;

D_ac = √(((2.5/2) - (1/2))² + 1.8²)

D_ac = 1.95 m

Also;

D_ad = √(((2.5/2) + (1/2))² + 1.8²)

D_ad = 2.51 m

I_a and I_b are put of phase by 180°. Thus, due to a and b, the flux linkages to c and d is given as;

φ_cd = 4 x 10^(-7)I_a( ln (2.51/1.95))

Mutual inductance per km is given as;

M = φ_cd/I_a

Thus;

M = 4 x 10^(-7)( ln (2.51/1.95))

M = 1.01 × 10^(-7) H/m

Per km;

M = 1.01 × 10^(-7) × 1000

M = 1.01 × 10^(-4) H/km

B) voltage per km is gotten by;

v_cd = ωMI

Now, ω = 2πf = 2π × 60 = 377 rad/s

Thus;

v_cd = 377 × 1.01 × 10^(-4) × 150

v_cd = 5.712 V/km

Thank you for your visit. We're dedicated to helping you find the information you need, whenever you need it. We hope you found this helpful. Feel free to come back anytime for more accurate answers and updated information. Westonci.ca is committed to providing accurate answers. Come back soon for more trustworthy information.