Welcome to Westonci.ca, the place where your questions find answers from a community of knowledgeable experts. Connect with a community of professionals ready to help you find accurate solutions to your questions quickly and efficiently. Explore comprehensive solutions to your questions from knowledgeable professionals across various fields on our platform.
Sagot :
Answer:
Explanation:
A multipurpose transformer can act as step up as well as step down transformer according to the desired setting by a user.
When the voltage at the output is greater than the voltage at the input of the transformer then it acts as step-up transformer and vice-versa acting is a step down transformer.
Given that:
input (primary) voltage of the transformer, [tex]V_i=220~V[/tex]
no. of turns in the primary coil, [tex]N_i=230[/tex]
- When the output voltage is 5.60 V:
[tex]V_o=5.60~V[/tex]
[tex]\frac{N_i}{N_o} =\frac{V_i}{V_o}[/tex]
[tex]\frac{N_o}{230}=\frac{5.60}{220}[/tex]
[tex]N_o=5.85\approx 6[/tex] turns compensating the losses
- When the output voltage is 12.0 V:
[tex]V_o=12.0~V[/tex]
[tex]\frac{N_i}{N_o} =\frac{V_i}{V_o}[/tex]
[tex]\frac{N_o}{230}=\frac{12.0}{220}[/tex]
[tex]N_o=12.45\approx 13[/tex] turns compensating the losses
- When the output voltage is 480 V:
[tex]V_o=480~V[/tex]
[tex]\frac{N_i}{N_o} =\frac{V_i}{V_o}[/tex]
[tex]\frac{N_o}{230}=\frac{480}{220}[/tex]
[tex]N_o=501.8\approx 502[/tex] turns compensating the losses
We hope our answers were helpful. Return anytime for more information and answers to any other questions you may have. We hope you found what you were looking for. Feel free to revisit us for more answers and updated information. Thank you for visiting Westonci.ca. Stay informed by coming back for more detailed answers.