Explore Westonci.ca, the leading Q&A site where experts provide accurate and helpful answers to all your questions. Connect with a community of experts ready to provide precise solutions to your questions on our user-friendly Q&A platform. Our platform offers a seamless experience for finding reliable answers from a network of knowledgeable professionals.

An industrial load with an operating voltage of 480/0° V is connected to the power system. The load absorbs 120 kW with a lagging power factor of 0.77. Determine the size of the capacitor in vars that is necessary to raise the power factor to 0.9 lagging.

Sagot :

Answer:

[tex]Q=41.33 KVAR\ \\at\\\ 480 Vrms[/tex]

Explanation:

From the question we are told that:

Voltage [tex]V=480/0 \textdegree V[/tex]

Power [tex]P=120kW[/tex]

Initial Power factor [tex]p.f_1=0.77 lagging[/tex]

Final Power factor [tex]p.f_2=0.9 lagging[/tex]

Generally the equation for Reactive Power is mathematically given by

Q=P(tan \theta_2-tan \theta_1)

Since

[tex]p.f_1=0.77[/tex]

[tex]cos \theta_1 =0.77[/tex]

[tex]\theta_1=cos^{-1}0.77[/tex]

[tex]\theta_1=39.65 \textdegree[/tex]

And

[tex]p.f_2=0.9[/tex]

[tex]cos \theta_2 =0.9[/tex]

[tex]\theta_2=cos^{-1}0.9[/tex]

[tex]\theta_2=25.84 \textdegree[/tex]

Therefore

[tex]Q=P(tan 25.84 \textdegree-tan 39.65 \textdegree)[/tex]

[tex]Q=120*10^3(tan 25.84 \textdegree-tan 39.65 \textdegree)[/tex]

[tex]Q=-41.33VAR[/tex]

Therefore

The size of the capacitor in vars that is necessary to raise the power factor to 0.9 lagging is

[tex]Q=41.33 KVAR\ \\at\\\ 480 Vrms[/tex]

We appreciate your time on our site. Don't hesitate to return whenever you have more questions or need further clarification. We appreciate your time. Please come back anytime for the latest information and answers to your questions. Get the answers you need at Westonci.ca. Stay informed with our latest expert advice.