At Westonci.ca, we provide clear, reliable answers to all your questions. Join our vibrant community and get the solutions you need. Join our platform to connect with experts ready to provide detailed answers to your questions in various areas. Get immediate and reliable solutions to your questions from a community of experienced professionals on our platform.

An industrial load with an operating voltage of 480/0° V is connected to the power system. The load absorbs 120 kW with a lagging power factor of 0.77. Determine the size of the capacitor in vars that is necessary to raise the power factor to 0.9 lagging.

Sagot :

Answer:

[tex]Q=41.33 KVAR\ \\at\\\ 480 Vrms[/tex]

Explanation:

From the question we are told that:

Voltage [tex]V=480/0 \textdegree V[/tex]

Power [tex]P=120kW[/tex]

Initial Power factor [tex]p.f_1=0.77 lagging[/tex]

Final Power factor [tex]p.f_2=0.9 lagging[/tex]

Generally the equation for Reactive Power is mathematically given by

Q=P(tan \theta_2-tan \theta_1)

Since

[tex]p.f_1=0.77[/tex]

[tex]cos \theta_1 =0.77[/tex]

[tex]\theta_1=cos^{-1}0.77[/tex]

[tex]\theta_1=39.65 \textdegree[/tex]

And

[tex]p.f_2=0.9[/tex]

[tex]cos \theta_2 =0.9[/tex]

[tex]\theta_2=cos^{-1}0.9[/tex]

[tex]\theta_2=25.84 \textdegree[/tex]

Therefore

[tex]Q=P(tan 25.84 \textdegree-tan 39.65 \textdegree)[/tex]

[tex]Q=120*10^3(tan 25.84 \textdegree-tan 39.65 \textdegree)[/tex]

[tex]Q=-41.33VAR[/tex]

Therefore

The size of the capacitor in vars that is necessary to raise the power factor to 0.9 lagging is

[tex]Q=41.33 KVAR\ \\at\\\ 480 Vrms[/tex]