Answered

Find the best solutions to your questions at Westonci.ca, the premier Q&A platform with a community of knowledgeable experts. Discover a wealth of knowledge from experts across different disciplines on our comprehensive Q&A platform. Our platform offers a seamless experience for finding reliable answers from a network of knowledgeable professionals.

A commercial customer calls. There is no air-conditioning in the upstairs office. This is a three-story building with an air handler on each floor and a chiller in the basement. The service technician arrives and politely introduces himself to the customer. After handing the customer a busi-ness card and describing the service he can provide, the technician asks some pertinent questions using everyday language the customer can understand. The technician then carefully listens and makes the customer feel like part of the solution to the service call problem. Once the technician has permission to enter the building, he goes to the fan room where the complaint is. There is no need to go to the chiller or the other floors because there would be complaints if the chiller was not providing cooling to those locations. The chilled water coil piping feels cold; the chiller is definitely running and furnishing cold water to the coil. The fan motor is not running. SAFETY PRECAUTION: Because the motor may have electrical problems, the technician proceeds with caution by opening, locking, and tagging the electrical disconnect. The technician pushes the reset button on the fan motor starter and hears the ratchet mechanism reset. The motor will not try to start while the technician is pushing the reset button because the disconnect switch is open. The unit must have been pulling too much current for the overload to trip. Using a digital multimeter, the technician checks for a ground by touching one lead to a ground terminal and the other to one of the motor leads on the load side of the starter. The meter is set on ohms and will detect a fairly high resistance to ground. See Figure 20.23 for an example of a motor ground check. Figure 20.23 SAFETY PRECAUTION: Any measurable resistance displayed when the meter's leads are connected between ground and the motor lead would indicate a ground—so caution is necessary. If the meter reads little to no resistance, the circuit should not be energized until the ground is cleared up